Just so I am clear since all schematics show the commons connected to 5vdc. Can I connect 24vdc to the common on the acorn board?
My relays are all 24vdc.
See my pic. Is this okay?
Acorn output 3 - 8 wiring 24vdc?
Moderator: cnckeith
-
- Posts: 595
- Joined: Tue Sep 12, 2017 10:03 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 1030090099
- DC3IOB: Yes
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: No
- Location: Outside Winston-Salem, NC
- Contact:
Acorn output 3 - 8 wiring 24vdc?
- Attachments
-
- acorn relay pic.PNG (15.05 KiB) Viewed 2407 times
Clay
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
-
- Posts: 100
- Joined: Mon Mar 03, 2014 4:24 pm
- Allin1DC CNC Controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
Re: Acorn output 3 - 8 wiring 24vdc?
All the terminals marked "COM" on the ACORN board are connected together and are connected to the 24V com (-V or GND) of the power supply. The schematics show the 5vdc common (GND) connected to the "COM" terminals, not the +5vdc. You can not connect +5vdc or +24vdc to the "COM" terminals or you will short out the power supply and damage the ACORN board. Since your relays are 24vdc you would connect +24vdc from the ACORN power supply to the VCC terminal of the relay board and the the other side of the relay coils would connect to the output terminals. All the output terminals pull down to "COM" (GND) to turn on.
Last edited by Centroid_Tech2 on Fri Nov 17, 2017 5:21 pm, edited 1 time in total.
When requesting support READ THIS POST first. viewtopic.php?f=60&t=1043
Please ALWAYS post a FRESH report. To make a report: https://www.youtube.com/watch?v=Ecvg0VJp1oQ.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
Please ALWAYS post a FRESH report. To make a report: https://www.youtube.com/watch?v=Ecvg0VJp1oQ.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
-
- Posts: 595
- Joined: Tue Sep 12, 2017 10:03 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 1030090099
- DC3IOB: Yes
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: No
- Location: Outside Winston-Salem, NC
- Contact:
Re: Acorn output 3 - 8 wiring 24vdc?
Thank you. I thought this was suspect.Centroid_Tech2 wrote: ↑Fri Nov 17, 2017 4:07 pm All the terminals marked "COM" on the ACORN board are connected together and are connected to the 24V com (-V or GND) of the power supply. The schematics show the 5vdc common (GND) connected to the "COM" terminals, not the +5vdc. You can not connect +5vdc or +24vdc to the "COM" terminals or you will short out the power supply and damage the ACORN board. Since your relays are 24vdc you would connect +24vdc from the ACORN power supply to the VCC terminal of the relay board and the the other side of the relay coils would connect to the output terminals. All the output terminals pull down to "COM" (GND) to turn on.
That's what I get for doing this schematic while on vacation!
Clay
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
-
- Posts: 9914
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Acorn output 3 - 8 wiring 24vdc?
They beat me to it!frijoli wrote: ↑Fri Nov 17, 2017 5:03 pmThank you. I thought this was suspect.Centroid_Tech2 wrote: ↑Fri Nov 17, 2017 4:07 pm All the terminals marked "COM" on the ACORN board are connected together and are connected to the 24V com (-V or GND) of the power supply. The schematics show the 5vdc common (GND) connected to the "COM" terminals, not the +5vdc. You can not connect +5vdc or +24vdc to the "COM" terminals or you will short out the power supply and damage the ACORN board. Since your relays are 24vdc you would connect +24vdc from the ACORN power supply to the VCC terminal of the relay board and the the other side of the relay coils would connect to the output terminals. All the output terminals pull down to "COM" (GND) to turn on.
That's what I get for doing this schematic while on vacation!
Frijoli....I did a video on that board!
https://youtu.be/tc8MYGzEFAY
At least you asked before you fired it up!
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 595
- Joined: Tue Sep 12, 2017 10:03 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 1030090099
- DC3IOB: Yes
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: No
- Location: Outside Winston-Salem, NC
- Contact:
Re: Acorn output 3 - 8 wiring 24vdc?
I saw the video Marty! I understood it when I saw the video, but when I looked at the Acorn schematics, they were all 5vdc. I couldn't get my mind wrapped around on how the circuit was completed when connected to 24vdc. Needless to say I wasn't comfortable with what I had drawn, so I waited. LOLmartyscncgarage wrote: ↑Fri Nov 17, 2017 6:47 pmThey beat me to it!frijoli wrote: ↑Fri Nov 17, 2017 5:03 pmThank you. I thought this was suspect.Centroid_Tech2 wrote: ↑Fri Nov 17, 2017 4:07 pm All the terminals marked "COM" on the ACORN board are connected together and are connected to the 24V com (-V or GND) of the power supply. The schematics show the 5vdc common (GND) connected to the "COM" terminals, not the +5vdc. You can not connect +5vdc or +24vdc to the "COM" terminals or you will short out the power supply and damage the ACORN board. Since your relays are 24vdc you would connect +24vdc from the ACORN power supply to the VCC terminal of the relay board and the the other side of the relay coils would connect to the output terminals. All the output terminals pull down to "COM" (GND) to turn on.
That's what I get for doing this schematic while on vacation!
Frijoli....I did a video on that board!
At least you asked before you fired it up!
Clay
PS. once I got the response, I tested what I was doing and it worked great. Accept I can't reverse my DC motor with the board I have.
KBMG and SIMG.
Clay
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/