ethernet communication errors...wits end

Post by pescadoman »

Firts off, everything works with the VCP. Both axis and the spindle. The problem occurs when I run g(s seem to work fine) commands. I configured the PC, but figured I may have gotten something wrong, so I took another PC that I've been using flawlessly for years and am having the same errors. I've never done a lathe before...btw. The cable is the stock one from Centroid. My next move, I suppose, is going to be grabbing a known good cable. I've attached a report. Thanks to everyone willing to help
Attachments
report_0479B7F04C20-0204202937_2024-05-04_13-09-14.zip
(846 KiB) Downloaded 4 times
ShawnM
Posts: 2275
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: ethernet communication errors...wits end

Post by ShawnM »

Have a look at your error report, it's no wonder nothing works. Here's a sample of your error log below. Dive into tech bulletin 270 and 309 and find out where your noise is coming from. Post pics of your cabinet wiring. Are you using shielded wire where it's recommended/required?

Code: Select all

(4)   05-04-2024 12:59:49 4032 Reset Cleared 
(1)   05-04-2024 12:59:53 304 MDI...
(4)   05-04-2024 12:59:55 944 MPU requested resend # 22
(4)   05-04-2024 12:59:55 946 PC resending # 958 
(1)   05-04-2024 13:00:05 327 Fault:  job cancelled
(4)   05-04-2024 13:00:05 9033 Reset Initiated, Press Reset to Clear
(4)   05-04-2024 13:00:07 4032 Reset Cleared 
(4)   05-04-2024 13:00:10 944 MPU requested resend # 23
(4)   05-04-2024 13:00:10 946 PC resending # 960 
(1)   05-04-2024 13:01:06 307 Operator abort:  job cancelled
(4)   05-04-2024 13:01:31 944 MPU requested resend # 24
(4)   05-04-2024 13:01:31 946 PC resending # 961 
(4)   05-04-2024 13:01:31 946 PC resending # 962 
(4)   05-04-2024 13:01:49 944 MPU requested resend # 25
(4)   05-04-2024 13:01:49 946 PC resending # 964 
(1)   05-04-2024 13:01:49 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   05-04-2024 13:02:22 944 MPU requested resend # 26
(4)   05-04-2024 13:02:22 946 PC resending # 966 
(4)   05-04-2024 13:02:39 944 MPU requested resend # 27
(1)   05-04-2024 13:02:39 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   05-04-2024 13:02:39 946 PC resending # 968 
(4)   05-04-2024 13:03:07 944 MPU requested resend # 28
(4)   05-04-2024 13:03:08 946 PC resending # 970 
(1)   05-04-2024 13:03:08 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   05-04-2024 13:03:15 944 MPU requested resend # 29
(4)   05-04-2024 13:03:15 946 PC resending # 972 
(4)   05-04-2024 13:03:33 944 MPU requested resend # 30
(4)   05-04-2024 13:03:33 946 PC resending # 974 
(4)   05-04-2024 13:04:26 944 MPU requested resend # 31
(1)   05-04-2024 13:04:26 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   05-04-2024 13:04:26 946 PC resending # 976 
(4)   05-04-2024 13:05:21 944 MPU requested resend # 32
(4)   05-04-2024 13:05:21 946 PC resending # 978 
(4)   05-04-2024 13:06:07 944 MPU requested resend # 33
(4)   05-04-2024 13:06:07 946 PC resending # 980 
(4)   05-04-2024 13:07:25 944 MPU requested resend # 34
(4)   05-04-2024 13:07:25 946 PC resending # 981 
(4)   05-04-2024 13:07:25 946 PC resending # 982 
(4)   05-04-2024 13:07:29 944 MPU requested resend # 35
(4)   05-04-2024 13:07:29 946 PC resending # 984 
(4)   05-04-2024 13:07:34 944 MPU requested resend # 36
(4)   05-04-2024 13:07:34 946 PC resending # 986 
(4)   05-04-2024 13:07:51 944 MPU requested resend # 37
(4)   05-04-2024 13:07:51 946 PC resending # 988 
(4)   05-04-2024 13:08:01 944 MPU requested resend # 38
(4)   05-04-2024 13:08:01 946 PC resending # 989 
(4)   05-04-2024 13:08:01 946 PC resending # 990 
(4)   05-04-2024 13:08:09 944 MPU requested resend # 39
(4)   05-04-2024 13:08:09 946 PC resending # 992 
(4)   05-04-2024 13:08:09 944 MPU requested resend # 40
(4)   05-04-2024 13:08:10 946 PC resending # 994 
(4)   05-04-2024 13:08:17 944 MPU requested resend # 41
(4)   05-04-2024 13:08:17 946 PC resending # 996 
(4)   05-04-2024 13:08:56 944 MPU requested resend # 42
(4)   05-04-2024 13:08:56 946 PC resending # 998 
(1)   05-04-2024 13:09:14 Creating report...
Gary Campbell
Posts: 2213
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: ethernet communication errors...wits end

Post by Gary Campbell »

Go to the LAN adapters mfgr website and update the driver(s)
GCnC Control
CNC Control & Retrofits
https://www.youtube.com/user/Islaww1/videos
pescadoman
Posts: 113
Joined: Wed Feb 12, 2020 3:18 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: USA

Re: ethernet communication errors...wits end

Post by pescadoman »

ShawnM wrote: Sat May 04, 2024 6:25 pm Have a look at your error report, it's no wonder nothing works. Here's a sample of your error log below. Dive into tech bulletin 270 and 309 and find out where your noise is coming from. Post pics of your cabinet wiring. Are you using shielded wire where it's recommended/required?

Code: Select all

(4)   05-04-2024 12:59:49 4032 Reset Cleared 
(1)   05-04-2024 12:59:53 304 MDI...
(4)   05-04-2024 12:59:55 944 MPU requested resend # 22
(4)   05-04-2024 12:59:55 946 PC resending # 958 
(1)   05-04-2024 13:00:05 327 Fault:  job cancelled
(4)   05-04-2024 13:00:05 9033 Reset Initiated, Press Reset to Clear
(4)   05-04-2024 13:00:07 4032 Reset Cleared 
(4)   05-04-2024 13:00:10 944 MPU requested resend # 23
(4)   05-04-2024 13:00:10 946 PC resending # 960 
(1)   05-04-2024 13:01:06 307 Operator abort:  job cancelled
(4)   05-04-2024 13:01:31 944 MPU requested resend # 24
(4)   05-04-2024 13:01:31 946 PC resending # 961 
(4)   05-04-2024 13:01:31 946 PC resending # 962 
(4)   05-04-2024 13:01:49 944 MPU requested resend # 25
(4)   05-04-2024 13:01:49 946 PC resending # 964 
(1)   05-04-2024 13:01:49 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   05-04-2024 13:02:22 944 MPU requested resend # 26
(4)   05-04-2024 13:02:22 946 PC resending # 966 
(4)   05-04-2024 13:02:39 944 MPU requested resend # 27
(1)   05-04-2024 13:02:39 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   05-04-2024 13:02:39 946 PC resending # 968 
(4)   05-04-2024 13:03:07 944 MPU requested resend # 28
(4)   05-04-2024 13:03:08 946 PC resending # 970 
(1)   05-04-2024 13:03:08 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   05-04-2024 13:03:15 944 MPU requested resend # 29
(4)   05-04-2024 13:03:15 946 PC resending # 972 
(4)   05-04-2024 13:03:33 944 MPU requested resend # 30
(4)   05-04-2024 13:03:33 946 PC resending # 974 
(4)   05-04-2024 13:04:26 944 MPU requested resend # 31
(1)   05-04-2024 13:04:26 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   05-04-2024 13:04:26 946 PC resending # 976 
(4)   05-04-2024 13:05:21 944 MPU requested resend # 32
(4)   05-04-2024 13:05:21 946 PC resending # 978 
(4)   05-04-2024 13:06:07 944 MPU requested resend # 33
(4)   05-04-2024 13:06:07 946 PC resending # 980 
(4)   05-04-2024 13:07:25 944 MPU requested resend # 34
(4)   05-04-2024 13:07:25 946 PC resending # 981 
(4)   05-04-2024 13:07:25 946 PC resending # 982 
(4)   05-04-2024 13:07:29 944 MPU requested resend # 35
(4)   05-04-2024 13:07:29 946 PC resending # 984 
(4)   05-04-2024 13:07:34 944 MPU requested resend # 36
(4)   05-04-2024 13:07:34 946 PC resending # 986 
(4)   05-04-2024 13:07:51 944 MPU requested resend # 37
(4)   05-04-2024 13:07:51 946 PC resending # 988 
(4)   05-04-2024 13:08:01 944 MPU requested resend # 38
(4)   05-04-2024 13:08:01 946 PC resending # 989 
(4)   05-04-2024 13:08:01 946 PC resending # 990 
(4)   05-04-2024 13:08:09 944 MPU requested resend # 39
(4)   05-04-2024 13:08:09 946 PC resending # 992 
(4)   05-04-2024 13:08:09 944 MPU requested resend # 40
(4)   05-04-2024 13:08:10 946 PC resending # 994 
(4)   05-04-2024 13:08:17 944 MPU requested resend # 41
(4)   05-04-2024 13:08:17 946 PC resending # 996 
(4)   05-04-2024 13:08:56 944 MPU requested resend # 42
(4)   05-04-2024 13:08:56 946 PC resending # 998 
(1)   05-04-2024 13:09:14 Creating report...
Attachments
20240504_132850.jpg
eng199
Posts: 382
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: ethernet communication errors...wits end

Post by eng199 »

Try CNC12 v5.10.
Fix #56 in the release notes may resolve resend errors.
Don't forget to plug the Ethernet cable back in after the photo.
Richards
Posts: 694
Joined: Sun Sep 16, 2018 9:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: South Jordan, UT

Re: ethernet communication errors...wits end

Post by Richards »

Tell us about your computer. Do you have WiFi enabled? Is it a laptop? Have you followed the instructions to prepare your PC for use with the Acorn?
-Mike Richards
pescadoman
Posts: 113
Joined: Wed Feb 12, 2020 3:18 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: USA

Re: ethernet communication errors...wits end

Post by pescadoman »

Richards wrote: Mon May 06, 2024 8:58 am Tell us about your computer. Do you have WiFi enabled? Is it a laptop? Have you followed the instructions to prepare your PC for use with the Acorn?
wifi is enable. I ran the pc tuner and configured according to the instructions. I switched to a know good computer, that I've used for years and still seem to be getting random errors. The machine is across the city and I forgot a usb stick to get a report. I"ve tried 2 computers. One is a Dell, one is a HP. Both are SFF's,
ShawnM
Posts: 2275
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: ethernet communication errors...wits end

Post by ShawnM »

We need a report to answer any questions. Disable wi-fi as it's not needed for Acorn. I'm guessing it's a noise issue.

FYI, the gauge of those red wires in your pic is extreme overkill. It's looks like residential wire anyway.
cnckeith
Posts: 7439
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: ethernet communication errors...wits end

Post by cnckeith »

use v5.1 there are ethernet connection improvements for intel drivers in v5.1