Enable outputs on Acorn

Posted: Thu Apr 25, 2024 8:05 am
by kman1967
I am using a DB25 interface for my stepper motor outputs. While using this are the enable outputs on H2 and H3 still active to use?

If so are the active high or low for enabled?

Re: Enable outputs on Acorn

Posted: Thu Apr 25, 2024 8:48 am
by Centroid_Tech2
When selecting the D25 connections in the wizard the behavior of the "Enable" terminals on H2 and H3 are inverted since most stepper drives are enabled by default and need a signal to disable them.Therefore these outputs are pulled low when the axis is NOT enabled. This behavior can be changed in the Advanced Axis Configuration menu.
AdvancedAxisConfig.JPG

Re: Enable outputs on Acorn

Posted: Thu Apr 25, 2024 9:11 am
by ShawnM
kman1967 wrote: Thu Apr 25, 2024 8:05 am I am using a DB25 interface for my stepper motor outputs. While using this are the enable outputs on H2 and H3 still active to use?

If so are the active high or low for enabled?
Please tell us what stepper drive you are using, most stepper drives are enabled by default and the ENA connection is not needed.

Re: Enable outputs on Acorn

Posted: Thu Apr 25, 2024 9:28 am
by kman1967
Thanks guys. That's the info I need. Although the drives are enabled by default, I am looking to disable them when required.

Re: Enable outputs on Acorn

Posted: Thu Apr 25, 2024 4:05 pm
by Gary Campbell
Although the drives are enabled by default, I am looking to disable them when required
.

Can you explain when that would be?

Re: Enable outputs on Acorn

Posted: Thu Apr 25, 2024 4:51 pm
by tblough
If you disable drives on an Acorn, you will have to re-home everytime you re-enable the drives. Acorn is an open-loop system.

Re: Enable outputs on Acorn

Posted: Thu Apr 25, 2024 9:12 pm
by ShawnM
Yes, what he's talking about doing makes no sense at all. Hopefully he'll elaborate on the "why".

Re: Enable outputs on Acorn

Posted: Mon Apr 29, 2024 6:51 am
by kman1967
This machine is in our R&D department. As part of the hazard assessment, one of the requirements is the disabling of the drives. It a requirement stipulated by our safety team which I don't have much say in. Honestly, I have found over time it's best just to do than to argue, less headaches.

Re: Enable outputs on Acorn

Posted: Mon Apr 29, 2024 8:16 am
by Nigelo
If you have a properly configured E-Stop, this will already do the job or am I missing something?

Re: Enable outputs on Acorn

Posted: Mon Apr 29, 2024 9:40 am
by cncsnw
I agree with Nigelo. Foremost, your emergency stop circuit should remove power from the stepper drivers. That should reliably ensure that the motors are free of power and torque whenever emergency stop is pressed.