Spindle turns starts on CNC12 boot up. (Resolved)

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

routebot
Posts: 26
Joined: Wed Aug 08, 2018 9:47 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Spindle turns starts on CNC12 boot up.

Post by routebot »

As mentioned above my problem was the VFD was running before the CNC12 was booted.
martyscncgarage
Posts: 9915
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Spindle turns starts on CNC12 boot up.

Post by martyscncgarage »

routebot wrote: Fri Mar 06, 2020 11:23 am As mentioned above my problem was the VFD was running before the CNC12 was booted.
At what point does it start running??
We need to SEE how you have things wired/connected, what schematic did you use?
What VFD make and model are you using?
Pictures of your control cabinet would be helpful
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
routebot
Posts: 26
Joined: Wed Aug 08, 2018 9:47 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Spindle turns starts on CNC12 boot up.

Post by routebot »

Here is the Delta VFD diagram. Currently I have Acorn Vout connected to AVI and COM going to ACM.
Attachments
delta VFD B.jpg
cncsnw
Posts: 3898
Joined: Wed Mar 24, 2010 5:48 pm

Re: Spindle turns starts on CNC12 boot up.

Post by cncsnw »

How do you have your forward run command (FWD) wired to the digital signal common (DCM)?

That needs to be controlled by a PLC output relay.

Also, how do you guarantee that the spindle cannot run when you press Emergency Stop, regardless of what may happen with the PLC signals? This is ideally done by cutting off AC power to the VFD, but is often just another link in the DCM -> FWD circuit (e.g., a circuit that runs from DCM, through the emergency stop contactor, through a PLC output relay or two, and back to FWD).

If you do not have a hardware emergency stop pushbutton; or you do not have a hardware emergency stop contactor or relay; or you do not have the spindle run command routed through a PLC output; then you need to review the sample wiring diagrams and come up with a new design.
slodat
Posts: 793
Joined: Thu Apr 12, 2018 11:16 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Spindle turns starts on CNC12 boot up.

Post by slodat »

Please post some info about your machine, how it is wired, report, photos, etc. We can't see what you are working on.
martyscncgarage
Posts: 9915
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Spindle turns starts on CNC12 boot up.

Post by martyscncgarage »

See attached example schematic of what Marc is explaining.
Marty
Attachments
S14953-ACORN_rev4_STANDARD_CONNECTIONS.pdf
(164.02 KiB) Downloaded 108 times
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
routebot
Posts: 26
Joined: Wed Aug 08, 2018 9:47 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Spindle turns starts on CNC12 boot up.

Post by routebot »

I had a chassis ground that was inadvertently connected the the DCM causing crazy stuff to happen.

My wiring is per the Acorn circuit diagram except I have a C86 board to deal with the CNCdrive drives. The C86 was using the output relay #1 to signal the C86 to activate. The C86 then sends a signal to input #5 " Drive Ok". To get around this I removed the C86 wires from output #1 and connected power to drive the contactor per the Acorn circuit diagram. My contactor is 3 phase so I connected the C86 signal wire to the spare contactor terminal. This allowed the contactor to switch on the C86 signal instead of the #1 output relay. Problem solved.

This router and VFD were in use with Mach4. I'm just updating to Acorn control. It seems like the spindle is fluctuating. It's been over a year since it last ran and I don't remember having this issue. Is this common with Acorn? Here is a video:
Gary Campbell
Posts: 2224
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: Spindle turns starts on CNC12 boot up.

Post by Gary Campbell »

Are you using 18ga shielded twisted pair for the 0-10v?
GCnC Control
CNC Control & Retrofits
https://www.youtube.com/user/Islaww1/videos
routebot
Posts: 26
Joined: Wed Aug 08, 2018 9:47 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Spindle turns starts on CNC12 boot up.

Post by routebot »

I'm using 24ga shielded twisted pair. Shield grounded on one side of the VFD ground only. 15' run to the control box. It worked on the last setup.
frijoli
Posts: 595
Joined: Tue Sep 12, 2017 10:03 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 1030090099
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: No
Location: Outside Winston-Salem, NC
Contact:

Re: Spindle turns starts on CNC12 boot up.

Post by frijoli »

routebot wrote: Sat Mar 07, 2020 11:37 pm I had a chassis ground that was inadvertently connected the the DCM causing crazy stuff to happen.

My wiring is per the Acorn circuit diagram except I have a C86 board to deal with the CNCdrive drives. The C86 was using the output relay #1 to signal the C86 to activate. The C86 then sends a signal to input #5 " Drive Ok". To get around this I removed the C86 wires from output #1 and connected power to drive the contactor per the Acorn circuit diagram. My contactor is 3 phase so I connected the C86 signal wire to the spare contactor terminal. This allowed the contactor to switch on the C86 signal instead of the #1 output relay. Problem solved.

This router and VFD were in use with Mach4. I'm just updating to Acorn control. It seems like the spindle is fluctuating. It's been over a year since it last ran and I don't remember having this issue. Is this common with Acorn? Here is a video:
The main difference between Mach and Acorn, in my opinion is that, Acorn is very near the mechanical/electrical noise..(typical for most industrial controls) Mach is PC based motion control which is not reliable for software reasons and hardware reasons, and cannot be corrected.
Acorn, if wired correctly to alleviate noise will always be stable once it is stable.
Clay
near Winston-Salem, NC
unofficial ACORN fb group https://www.facebook.com/groups/897054597120437/
Post Reply