Error in RT-200 Manual wiring diagram?

All things related to Centroid Oak, Allin1DC, MPU11 and Legacy products

Moderator: cnckeith

Post Reply
tblough
Posts: 3072
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Error in RT-200 Manual wiring diagram?

Post by tblough »

Page 32 (DC wiring) in the RT-200 manual shows Encoder common (blk/red) connected to pin D of the Amphenol connector. The home switch green wire is also connected to pin D on the Amphenol connector. Is this correct?
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
Centroid_Tech
Posts: 286
Joined: Thu Mar 18, 2010 2:24 pm

Re: Error in RT-200 Manual wiring diagram?

Post by Centroid_Tech »

That is correct because the return for the power for the encoder signals should be the same as the return for the power for your inputs.
When requesting support, please ALWAYS post a current report. Find out how to take a report from your Acorn, CNC11 or CNC10 system here: https://www.youtube.com/watch?v=Ecvg0VJp1oQ.

If your question is PLC, Macro or program related, please also post a copy of the program or macro as well.

Without the above information we may not be able to help and/or reply until the required information is posted..