alarm 916
Posted: Mon Sep 18, 2017 4:40 pm
by mike
Anytime i use the MDI I get this fault can you help me?
Re: alarm 916
Posted: Tue Sep 19, 2017 7:20 am
by diycncscott
It says your estop is pressed.........................
Re: alarm 916
Posted: Tue Sep 19, 2017 8:23 am
by mike
The picture is just for the serial number I can run programs with no problem just when I try to use the MDI I to make a move to re zero I get this fault
Re: alarm 916
Posted: Tue Sep 19, 2017 8:54 am
by Centroid_Tech
It's most likely because parameter 11 is set to -14 rather than 14. From the main screen press F1(Setup)->F3(Config)->default password is 137->F3(Params). Change the value of parameter 11 and press F10(Save). See if that helps you out.
Re: alarm 916
Posted: Tue Sep 19, 2017 10:03 am
by mike
Parameter 11 is set to -14 rather than 14 ??
Re: alarm 916
Posted: Tue Sep 19, 2017 10:25 am
by mike
Nevermind normally open normally closed I read the manual thanks for the quick reply